Hello,
If you use OPC Scout (OPC client delivered on Simimatic Net DVD that you can use for test) instead or/off in parallel with WinCC, do you see all symbols in the SYM folder?
If not, verify in the tab "S7" of the OPC Server settings (in HWconfig in Step7) if you have either selected:
- use all symbols
- use configured symbols (but then you must add yourself the symbols that you want to see).
See also in the Simatic Net configuration console, in the folder OPC, if you refer to the symbol list exported by step7.
Be sure that you download HWconfig to the OPC server if you add new symbols.