Thread Starter: martinrelayer Started: 8/14/2012 4:12 PM Replies: 3
hellowe have several micromaster 440 frame sizes B, C, and D.I haven't found any maintenance document, only for f frames. Is there any?Is there a maintenance kit for frame sizes b, c, and d? I mean fans or capacitors, etc.I also would like to know if there's a capacitor reforming recommendation, and if there is any special procedure for spare drives of 6 years of storage in frames B, C, and D.regards.
hellowe have several micromaster 440 frame sizes B, C, and D.I haven't found any maintenance document, only for f frames. Is there any?Is there a maintenance kit for frame sizes b, c, and d? I mean fans or capacitors, etc.
What did you meant by maintenance kits?
I also would like to know if there's a capacitor reforming recommendation, and if there is any special procedure for spare drives of 6 years of storage in frames B, C, and D.
Please have a look on the procedure in this FAQ:
After what time period do the DC link capacitors have to be re-formed? What is the procedure when forming DC link capacitors?
Hope this helps.
I mean if theres some preventive maintenance directive.for example, changing fan coolers in drives. Other manufacturers specify every 5 years changing the fan coolers inside drives. I couldn't find any information about it, or perhaps the lifetime of a fan is the same than of the inverter electronics therefore there is no need to change fans. Always talking of A,B,C and D framesabout capacitors, i've found a graph for capacitor reforming in the manual.