LOGO!
Abput Sink / Source type DI in LOGO
Thread Starter: AmitC Started: 8/10/2012 4:08 PM Replies: 3

8/10/2012, 4:08 PM
|
Joined 11/29/2011
Last visit: 5/12/2013
Posts: 15
Rating:
(0)
|
(0)
|
Do LOGO PLC is having Sink / Source type Digital input?? If yes, then which module is having this facility? I want to take 8 digital i/p's as a sink type and 8 digital i/p's as a source type. Please suggest.
|
|
|
|

8/10/2012, 10:23 PM
|
Joined 4/29/2011
Last visit: 5/18/2013
Posts: 24
Rating:
(0)
|
(0)
|
HI,
I believe this is not possible with LOGO! alone. LOGO! only accepts source inputs. A set of 8 interfacing relays can be used to condition your sink inputs and allow you to proceed with your program. You are limited to 24 inputs remember.
|
|
|
|

8/11/2012, 9:29 PM
|
Joined 12/27/2006
Last visit: 5/17/2013
Posts: 415
Rating:
(20)
|
(0)
|
You can also place a resistance of about 1000 ohms between the + of your power and your digital input. Your sensor connects to the digital input and - supply. Then you can use Sink sensors.
|
|
|
|
|
Thank you for this post from:
|

8/20/2012, 9:41 AM
|
Joined 7/24/2006
Last visit: 5/16/2013
Posts: 1823
Rating:
(216)
|
(0)
|
´Hi,
you can use a LOGO! 24RC or 24RCo. This type of LOGO! supports 24V DC or 24V AC as power supply. If sink or source depends on how you wire it (Power supply and inputs).
This is also possible with the LOGO! DM8 24R.
Hope this helps
|
|
|
|
Actions