Dear Sirs,
Is it possible to run 1HU perminent field DC motor into field weakening mode with SIMOREG 6RA70?
In my understanding, I have to set P082 = 0: Internal field is not used. In case my motor rated speed is 1800rpm, tacho data is 20mVmin,i.e, 20V<-->1000rpm, does it mean that the max speed I can reach for this motor is 1800rpm, P083 = 1: The actual speed is supplied from the “Main actual value” channel (K0013) (terminals XT.103, XT.104) P741 Tacho voltage at maximum speed = 1800/1000*20=36V
Thanks and Regards
|
|
|
|

8/9/2012, 6:20 AM
|
Joined 8/25/2006
Last visit: 5/23/2013
Posts: 900
Rating:
(85)
|
(0)
|
Hello. If your motor is permanent-field, there will not be any field weakening mode, as you disable internal field in drive (P082=0). If your tacho 20V-1000rpm, then P741=36V is ok.
|
|
|
|