Dear Sirs,

Is it possible to run 1HU perminent field DC motor into field weakening mode with SIMOREG 6RA70?

In my understanding, I have to set P082 = 0: Internal field is not used.
In case my motor rated speed is 1800rpm, tacho data is 20mVmin,i.e, 20V<-->1000rpm,
does it mean that the max speed I can reach for this motor is 1800rpm,
P083 = 1: The actual speed is supplied from the “Main actual value” channel (K0013)
(terminals XT.103, XT.104)
P741 Tacho voltage at maximum speed = 1800/1000*20=36V

Thanks and Regards
Top
  8/9/2012, 6:20 AM
Joined 8/25/2006
Last visit: 5/23/2013
Posts: 900
Rating:
Rated: Excellent [4.2 out of 5 / rated 85 time(s)]. (85) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello.
If your motor is permanent-field, there will not be any field weakening mode, as you disable internal field in drive (P082=0). If your tacho 20V-1000rpm, then P741=36V is ok.
Top
  8/10/2012, 3:37 AM
Joined 8/3/2012
Last visit: 5/9/2013
Posts: 4
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
I see, thanks.