Analog Setpoint Holding
Thread Starter: Ashutosh Kr Started: 8/2/2012 6:56 AM Replies: 4

8/2/2012, 6:56 AM
|
Joined 3/15/2011
Last visit: 5/20/2013
Posts: 52
Rating:
(5)
|
(0)
|
Dear All,
I have 200 Kw (PM 240) Sinamics g120 drive having control card CU240 E-2 FIRMWARE VERSION 4.4.The setpoint is comming from analog source in the form of 4-20 mA.
The customer demands that in case the setpoint falls below 4 mA ,the drive should run as per last setpoint.i wanted to know wheather this can be achieved or not.I know this can be achived in case of motorised potentiomter.but can it be done i case of Analog input . Can this realised throgh FFB. My scaling values are 4mA= 25% speed 20mA=100% speed Please Help , i want your help desparately
Regards
|
|
|
|

8/2/2012, 11:24 AM
|
Joined 10/29/2007
Last visit: 4/24/2013
Posts: 651
Rating:
(41)
|
(0)
|
see p0756 to p0760
an example you´ll find in FAQ http://support.automation.siemens.com/WW/view/en/5127160 it´s written for MM420 but can be used for G120 (without the 300Ohm resistor)
Mit freundlichem Gruß / Best regards
Jens S
|
|
|
|

8/2/2012, 12:06 PM
|
Joined 3/15/2011
Last visit: 5/20/2013
Posts: 52
Rating:
(5)
|
(0)
|
HiJen S thanks for your prompt reply , but i have already commissioned the system ,it is running, but the customer is demanding that in case there is a wire brakage the the drive should run as per previou setpoint , im tring to implement this logic using FFB .Perhaps i can get help from your side too Hope this explians my problem Regards
|
|
|
|

8/2/2012, 3:27 PM

8/4/2012, 8:25 AM
|
Joined 3/15/2011
Last visit: 5/20/2013
Posts: 52
Rating:
(5)
|
(0)
|
Hi Jens S ,Thanks for your reply once again , i accomplised the task with the help of FFB .I'm attaching a copy so that i can be helpful for someone in future 
Regards
|
|
|
|