please help me.
 i have a simovert with order 6se7033-2eg60 .i replaced  a cuvc board in this drive.i done quick commissioning drive setting power section and all of my setting are ok. it is  terminals command and setpoint source . 
but i have bad problem when i run motor by terminal first vdc link 525vdc but afew second vdc 406vdc and drive displays f008 and stop motor.
i check all of  parameters vdc . my cuvc is new. i donot what do i?

I should fix the problem immediately please help me.
Top
  7/1/2012, 9:34 PM
Joined 6/4/2008
Last visit: 6/17/2013
Posts: 788
Rating:
Rated: Excellent [4.4 out of 5 / rated 229 time(s)]. (229) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
edison65 wrote:
 i have a simovert with order 6se7033-2eg60 .i replaced  a cuvc board in this drive.i done quick commissioning drive setting power section and all of my setting are ok. it is  terminals command and setpoint source . 
but i have bad problem when i run motor by terminal first vdc link 525vdc but afew second vdc 406vdc and drive displays f008 and stop motor.
i check all of  parameters vdc . my cuvc is new. i donot what do i?


Hi, please confirm if this problem (F008) existed before exchanging the CUVC card.

Also, it is not clear that the DC voltage you mention is measured (with a meter) from the DC actual, or if it is a parameter display (r006) please make sure that both match exactly.

I suspect that 1 phase of the rectifier is not functioning, it is possible for the DC Link voltage to reach full voltage with only two phases of the rectifier, HOWEVER, as soon as any load is present, the voltage drops sharply. I recommend using three current clamps on the input phases to determine which one is not drawing any (much) current and repair.

Regards,
Graeme



=== Edited by Graeme @ 7/4/2012 6:07 PM [GMT ] ===



There are 10 types of people . . .
Those who understand Binary, and those who don't.
Top
  7/4/2012, 11:22 AM
Joined 7/4/2011
Last visit: 4/27/2013
Posts: 22
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Pls. check thyrister triggering card(PCC). It may malfunction. Today My 75KW drive 6SE7031-8EF60-1AA1 was tripping on F008. I compared DC link voltage(with Volt meter) and r006, found same. Then replaced PCC card. Found drive is working OK.

But i have doubt that same PCC card's (6SE7031-7HH84-1HJ0) 2,4 & 6 SMD components are getting heated up. What may be the reason??
Top
  7/7/2012, 1:55 AM
Joined 12/18/2011
Last visit: 4/15/2013
Posts: 5
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 

 

Good analysis mr GraemeRnf:lblSmileyTooltip_

Top
Page 1 of 1 (4 items)
Actions