Thread Starter: tomorrow Started: 6/12/2012 1:34 PM Replies: 8

6/12/2012, 1:34 PM
|
Joined 4/20/2010
Last visit: 5/30/2013
Posts: 31
Rating:
(3)
|
(0)
|
Hi
I have the problem that if I add a variable to a Watchlist I have a 50% chance thats successfull und 50% that I get a problem with the Programm and siemens is telling me that the application has encountered an error so I need to restart the PC  In addition its unimportant if there is already one or more variables in this list...
Does someone have a little hint for me? because it's driving me crazy.... thanks...
|
|
|
|

6/13/2012, 7:58 AM
|
Joined 5/12/2006
Last visit: 6/19/2013
Posts: 1591
Rating:
(120)
|
(0)
|
Hello,
can you make a screenshot of the error message ? Which OS do you have installed?
Normaly is not needed to restart the pc when simotion scout crashes.
Regards Christoph
|
|
|
|

6/13/2012, 1:30 PM
|
Joined 4/20/2010
Last visit: 5/30/2013
Posts: 31
Rating:
(3)
|
(0)
|
since Today I have no problem ?!? strange but I will tell you if it cames back again... then with a little screenshot ;)
|
|
|
|

6/14/2012, 3:22 PM
|
Joined 6/14/2012
Last visit: 3/20/2013
Posts: 12
Rating:
(0)
|
(0)
|
Hiii tomorrow.....
Scout makes me surprise too with problems like you faced. Sometimes it happned that if we want to force variables from the watchtable or from the address list, they dosent get forced. then i need to write some logic and download it to make those variables high. The next day after removing that logic from the program and forcing the same variables from the address list, they were getting force by following exactly the same procedure which i did the other day. Strange!!
|
|
|
|

6/20/2012, 3:38 PM
|
Joined 4/20/2010
Last visit: 5/30/2013
Posts: 31
Rating:
(3)
|
(0)
|
Today the error came again and the Siemens Simotion Diagnostics opened... but I do not get an information what made this happen... have a look at the attached screenshot..
|
|
|
|

6/21/2012, 4:27 AM
|
Joined 5/12/2006
Last visit: 6/19/2013
Posts: 1591
Rating:
(120)
|
(0)
|
Hello,
under the path "C:\Documents and Settings\All Users\Application Data\Siemens\Simotion\Diagnostics\2.0.0.0" the Diagnostic Tool save more Informations of the crash. Can you post this data here ?
Regards Christoph
|
|
|
|

6/22/2012, 8:00 AM
|
Joined 4/20/2010
Last visit: 5/30/2013
Posts: 31
Rating:
(3)
|
(0)
|
ok there I have al lot of these crash folders :D they are from the older ones... what file would you like to see?
attached I have the ErrorReport.xml
best wishes
|
|
|
|

6/22/2012, 4:13 PM
|
Joined 5/12/2006
Last visit: 6/19/2013
Posts: 1591
Rating:
(120)
|
(0)
|
Hello,
i need the complete directory: C:\Documents and Settings\All Users\Application Data\Siemens\Simotion\Diagnostics\2.0.0.0\b73ca1e3-3b1b-40ef-8bc2-798ad2dd553e
Regards Christoph
|
|
|
|

6/25/2012, 7:54 AM
|
Joined 4/20/2010
Last visit: 5/30/2013
Posts: 31
Rating:
(3)
|
(0)
|
|
|
|
|
Actions