How to transfer many named connections from different PLC tags into MPI with different MPI addresses?

Thread Starter: KayBee   Started: 11/29/2011 6:56 AM   Replies: 2

« Previous thread Next thread »
Page 1 of 1 (3 items)
  11/29/2011, 6:56 AM
Joined 9/3/2007
Last visit: 5/23/2013
Posts: 224
Rating:
Rated: Outstanding [3.25 out of 5 / rated 4 time(s)]. (4) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
KayBee wrote:
There is no possibility to connect Tags under Named connection with PLCSIM.One way to do is to move the tags from Named connection to MPI. This can by done by:
1. Open WinCC Project
2.Open SQL Server Management Studio 2005, my case
3.Connect.
4.Then Open Database as attached-"Table1"
5.Then Exchange the channelnumber value as arrow marked in in the 2nd pic.CHUNITNUMBER
6. Now check Tag are exchanged between MPI & Named connection.

There may be difficulty doing with Structured tag, but may be some way should be there. This is just a way, not professional way to do.

Attachment: Table.zip  (59 Downloads)


Dear All,

I did a post last time for exchanging Tags between Named connection and MPI from SQL server, but I now I have multiple CPUs with Manynamed connections. How to transfer all these named connections from different PLC tags into MPI with different MPI addresses? Any Idea ?



=== Edited by O_Moderator @ 11/29/2011 10:27 AM [GMT ] ===
new subject after splitting from Connect WinCC V7.0 and PLCSim via Name connection


Regards,
KayBee

Top
  11/29/2011, 10:47 AM
Joined 10/5/2010
Last visit: 5/24/2013
Posts: 1368
Rating:
Rated: Outstanding [3.86 out of 5 / rated 36 time(s)]. (36) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello Kaybee,

as far as I know does PLCSIM not work with named connections.

Best regards

Bizur
Top
  5/28/2012, 3:21 PM
Joined 12/27/2011
Last visit: 1/4/2013
Posts: 7
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi everyone.
I have the same problem.
The solution I found is:
If you are using PCS7 - to move all tags to IE folder, you have to change Connection type during OS compilation.

I hope this info will be helpfull for someone.

Regards,
Ivan