Dear all,
I faced fault-30022 in sinamics drive which having simotion M-D435 and CU-320.what causes are responsible for this fault and how can i solve this fault please gauide me regardig to this.
Regards,
Vivek
|
|
|
|

5/25/2012, 11:37 AM
|
Joined 9/14/2007
Last visit: 4/9/2013
Posts: 33
Rating:
(2)
|
(1)
|
Dear Vivek,
Fault F30022 is basically for for defect in IGD card or short ckt or open the IGBT.you can check the IGBT with the help of multimeter with the help of attached file. Mostly i found problem with IGD or IGBT.
Regrads, Shank
|
|
|
|

5/25/2012, 12:25 PM
|
Joined 4/18/2012
Last visit: 5/22/2013
Posts: 20
Rating:
(0)
|
(0)
|
Dear shnak,
Actually I have no idea that how to perform the cold test of igbt? could u tell me before performing this test which connections i have to removed? is it possible any other reason is responsible for this fault-30022.?
Regards, Vivek
|
|
|
|

5/25/2012, 1:26 PM
|
Joined 9/14/2007
Last visit: 4/9/2013
Posts: 33
Rating:
(2)
|
(1)
|
Dear Vivek,
Remove the motor outgoing connection & DC link or Incoming AC supply connection . Switch OFF the Control as well as 24 VDC supply & then carried out cold run test. Normally if you check the fault causes it is due to damage of fibre optic cable or power cable connection opened, or otherwise because of IGD card or IGBT failure.
Regards, Shank
|
|
|
|

5/28/2012, 10:15 AM
|
Joined 4/18/2012
Last visit: 5/22/2013
Posts: 20
Rating:
(0)
|
(0)
|
Dear shank, Thanx your given information is very helpful.......
|
|
|
|