Im having trouble getting my PLC to work with my encoder.

I think it could be becasuse the encoder is a Sine/cosine encoder with 1Vss? Will the PLC read 1Vss?

Cheers Rnf:lblSmileyTooltip_
Top
  5/17/2012, 8:51 AM
Joined 9/28/2005
Last visit: 5/29/2013
Posts: 2912
Rating:
Rated: Excellent [4.02 out of 5 / rated 209 time(s)]. (209) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi,

In this manual SIMATIC S7-300 CPU 31xC and CPU 31x: Technical specifications chapter 8.7.6 page 292 you will find encoder selection criteria. See if it fits your need. Also this forum post could be of interest for you

FM350-2 works with encoders 1Vss sin/cos?


Regards,
--------------------------------
Darius
Automation engineer/programmer
Top
  5/17/2012, 10:22 AM
Joined 7/16/2006
Last visit: 6/19/2013
Posts: 1454
Rating:
Rated: Outstanding [3.47 out of 5 / rated 164 time(s)]. (164) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi
craiglb wrote:

Im having trouble getting my PLC to work with my encoder.
I think it could be becasuse the encoder is a Sine/cosine encoder with 1Vss?
Will the PLC read 1Vss?


You must convert 1Vss to 5VTTL.

Look for Heidenhain Untits named  "IBV101 "  or "APE371" or . . .


Regards Karl

Karl
Top
  5/17/2012, 11:46 AM
Joined 3/15/2008
Last visit: 6/18/2013
Posts: 4456
Rating:
Rated: Outstanding [3.89 out of 5 / rated 415 time(s)]. (415) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Gebhardt Karl wrote:
Hi
craiglb wrote:

Im having trouble getting my PLC to work with my encoder.
I think it could be becasuse the encoder is a Sine/cosine encoder with 1Vss?
Will the PLC read 1Vss?


You must convert 1Vss to 5VTTL.

Look for Heidenhain Untits named  "IBV101 "  or "APE371" or . . .


Regards Karl


No, you are wrong. blush

craiglb told us that he is using a 313C.

That can not use 5V. It needs 24V for the counter input signals.

Industrieautomation: Softwareerstellung und Inbetriebnahme weltweit.
http://www.ibn-service.com
Top
Thank you for this post from:
  5/17/2012, 12:17 PM
Joined 11/1/2010
Last visit: 6/10/2013
Posts: 19
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Thanks for your help Folks,

I've decided it was easier and probably cheaper to change over the encoder. I have chosen one that I have used in the past with a 313c PLC.  This one

Rnf:lblSmileyTooltip_