I have a system with 3 Micromaster MM440 drives.  They are all supposed to be setup the same and are all programmed the same in the PLC.  However, when 2 of these drives are not enabled the display on the drive flashes between 0hz and 30hz.   30hz is the speed reference that is being sent to the drive from the PLC.  This reference is always sent to the drive, even when not enabled.

The third drive does not oscilate between 0 and 30hz but it still receives a speed reference from the PLC when not enabled.  Any thoughts about what I need to change so that they all operate the same.  My customer does not care whether they all oscilate or all show 0hz when not enabled, but they want them all to be the same.

Thanks.
Top
  5/9/2012, 6:26 PM
Joined 3/15/2008
Last visit: 5/20/2013
Posts: 4434
Rating:
Rated: Outstanding [3.88 out of 5 / rated 409 time(s)]. (409) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 

Just set reference value to 0 when drives are not enabled.


Industrieautomation: Softwareerstellung und Inbetriebnahme weltweit.
http://www.ibn-service.com
Top
  5/9/2012, 7:02 PM
Joined 11/4/2010
Last visit: 5/14/2012
Posts: 2
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Setting the drive reference to 0 is not possible at this time.  Any other thoughts?
Top
  5/9/2012, 7:35 PM
Joined 5/28/2008
Last visit: 5/22/2013
Posts: 2187
Rating:
Rated: Outstanding [3.65 out of 5 / rated 431 time(s)]. (431) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Ben1855 wrote:
I have a system with 3 Micromaster MM440 drives.  They are all supposed to be setup the same and are all programmed the same in the PLC.  However, when 2 of these drives are not enabled the display on the drive flashes between 0hz and 30hz.   30hz is the speed reference that is being sent to the drive from the PLC.  This reference is always sent to the drive, even when not enabled.

The third drive does not oscilate between 0 and 30hz but it still receives a speed reference from the PLC when not enabled.  Any thoughts about what I need to change so that they all operate the same.  My customer does not care whether they all oscilate or all show 0hz when not enabled, but they want them all to be the same.

Thanks.
Hello,
Flashing between 0 & 30Hz (when ever PLC is sending 30 Hz) on the drive terminals is normal. The BOP wants to tell that there is a set point frequency can be read by terminals and the drive enable signal is not energized.
For the third drive, did you measured the setpoint signal using a multimeter? 
If there is a setpoint signal and the drive doesn't blinking between the corrseponding Hz of it and 0Hz, then there is something different between this drive and the other two drives.
You can use drive monitor to upload parameters from one of the two drives and then download it to the third one.
Hope this helps.


Ayman Elotaify
MISC Egypt
www.miscegypt.com
Top
  5/10/2012, 2:20 AM
Joined 7/8/2009
Last visit: 5/21/2013
Posts: 1167
Rating:
Rated: Excellent [4.25 out of 5 / rated 326 time(s)]. (326) 
Users with special expertise supervising conferences
Rated: Excellent [5 out of 5 / rated 1 time(s)]. (1) 
Ben1855 wrote:


The third drive does not oscilate between 0 and 30hz but it still receives a speed reference from the PLC when not enabled.  Any thoughts about what I need to change so that they all operate the same.  My customer does not care whether they all oscilate or all show 0hz when not enabled, but they want them all to be the same.

Thanks.


How you are so sure that 3rd drive is getting setpoint?

Are you able to run the drive? have you checked drive by giving start command? have you checked setpoint from Parameter? If you are using Profibus communicatio, then from r2050 you can see setpoint. Normally second PZD that is r2050.1 and if you use analog as setpoint check from r752

Also check setting in P006

Now everything is OK then I recommend you to do factoryset and recomission whole drive

Regards
Devesh Vithani

Please say Thanks if your Problem is Solved.. :-)