One of my S7400H on the plant acting strange: it's running much slower in redundant mode, then in solo mode (f.e. refreshing data when faceplate is opened, in solo mode: less the 1 second, in redundant mode: sometimes about 4 seconds).
Are you sure that WinCC connection has been configured as S7-Fault-tolerant connection?!
Just make sure you have this kind of connection and make sure that tags in WinCC are inside the named connection.
The CPU it not overloaded (about 30% load). I increased "Monitoring times" H Parameters in HW Config, I modified "Scan cycle load from communication" (increasing/decreasing) but it make no change in speed on CPU.
The CPU has lots of AS-wide interconnection.
Somebody has an idea what is going on?
What is your CPU and how many connection resources do you use?
Can you remove these AS connections and test the CPU with WinCC in this case?
Hello
I'm using opition "0" in "Cyclic Interrupt OB with Special Handling", I don't need it. I think that changing this options has no infuence on speed of CPU.
It's ok as you are using option 0. The special handling is mainly used with fail safe systems and it is not related to your problem.
Best regards,
H-H