Hi,
i've got problem with Simatic 505 CPU 555, the CPU Good Led is off, both CPU RUN and Battery Good are on.
I know there is a fatal error in the CPU based on system manual. I already try to reset with no battery back up but the CPU Good Led still off.
I want to online with Tisoft using real serial port on PC to CPU Port 1 to know the fatal error code but always time out.
I use the pin configuraton as follow :

1&4&6 are short on both connection
7&8 are short on both connection
2 - 3
3 - 2
5 - 5

and also try this configuration :

1&6----------------4
    4----------------1&6
    5----------------5
    2----------------3
    3----------------2
    7 & 8 Short in both connection

All dip switch are left (ON).
Please advise.

Regards,

Ciwa



=== Edited by ciwa79 @ 5/3/2012 2:07 PM [GMT ] ===


Top
  5/3/2012, 3:46 PM
Joined 2/10/2006
Last visit: 3/20/2013
Posts: 64
Rating:
Rated: Excellent [5 out of 5 / rated 3 time(s)]. (3) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
  • Did your programming cable work before ?
  • Try the CPU in another base with another Power Supply. Sometimes the CPU shows CPU good LED off but the problem is related to the PS.
  • If it still shows CPU good LED off, you may have a plain Hardware failure of the CPU. In that case replace it.

Carlo

Top
  5/3/2012, 11:00 PM
Joined 6/20/2007
Last visit: 5/23/2013
Posts: 402
Rating:
Rated: Excellent [4.16 out of 5 / rated 61 time(s)]. (61) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
There is a certain amount of capacitance in the CPU.  In addition to pulling the battery, pull the CPU out of the I/O rack if you didn't have to pull the CPU out to get the battery out.  The system manual has the pin out for the cable on page 5-5 and chapter 3 has the dip switch settings.  The communication time out is indicative of a CPU that is locked up.
Regards
billwest  

Attachment: 5x5sm.pdf  (6 Downloads)

Bill West
Consulting Sales Application Engineer
Siemens Industry, Inc.
Industry Automation
Industrial Automation Systems
1900 Musket Court
Stone Mountain, GA 30087
Work: 770-310-5965

Top
Thank you for this post from:
  5/4/2012, 6:34 AM
Joined 1/27/2009
Last visit: 5/6/2013
Posts: 24
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
SamTheEagle wrote:
  • Did your programming cable work before ?
  • Try the CPU in another base with another Power Supply. Sometimes the CPU shows CPU good LED off but the problem is related to the PS.
  • If it still shows CPU good LED off, you may have a plain Hardware failure of the CPU. In that case replace it.

Carlo


Hi Carlo,
- I've never test the cable before this is the first time.
- I only have new base and CPU, already try to replace CPU and base with the new one but CPU Good LED still off, i'll find the new power supply perhaps this is the problem.
Top
  5/4/2012, 6:40 AM
Joined 1/27/2009
Last visit: 5/6/2013
Posts: 24
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
billwest wrote:
There is a certain amount of capacitance in the CPU.  In addition to pulling the battery, pull the CPU out of the I/O rack if you didn't have to pull the CPU out to get the battery out.  The system manual has the pin out for the cable on page 5-5 and chapter 3 has the dip switch settings.  The communication time out is indicative of a CPU that is locked up.
Regards
billwest  

Hi Billwest,
I already try to reset the fatal error as decsribes in the system manual chapter 9 and replace the CPU and Base with the new one. But the problem still exist.
What is the correct pin out cable?

Top
  5/4/2012, 7:03 AM
Joined 4/30/2008
Last visit: 5/25/2013
Posts: 628
Rating:
Rated: Outstanding [3.94 out of 5 / rated 36 time(s)]. (36) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 


Billwest sent you the manual with the connections in it but here is the page you need
It's a rs232 cross over cable


Attachment: 5x5sm[1].pdf  (8 Downloads)