Technical Forum

SIMODRIVE Converter system

Profibus DP Question!

Thread Starter: Hezzens_Z   Started: 6/7/2010 11:03 AM   Replies: 5

« Previous thread Next thread »
Page 1 of 1 (6 items)
  6/7/2010, 11:03 AM
Joined 9/10/2009
Last visit: 8/24/2010
Posts: 17
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Good morning (if you live in europe ^^)

I have the following problem.
I have 3 pumps with simodrive that is connected on Profibus DP.
My software is working properly and the hardware is installed correctly but my pumps will not work.

So I want to check out the profibus DP signal, so I can determine the problem.
Is there an manual for this?

PS I already have a PG with CP5611 and Amperolyzer V3.0
Top
  6/7/2010, 11:27 AM
Joined 3/21/2006
Last visit: 5/14/2013
Posts: 9063
Rating:
Rated: Outstanding [3.78 out of 5 / rated 820 time(s)]. (820) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello,

Even without Amperolyzer V3.0 you could detect Profibus failure. In the beginning you could check if you send commands to the drives. Also is possible if you receive commands into the drive. About how to use Amprolyzer look at documentation there AmprolyzerV32.zip

Best regards,
Hristo Mihalev
Top
  6/7/2010, 11:57 AM
Joined 9/10/2009
Last visit: 8/24/2010
Posts: 17
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Thank you for your reply.

But the help file of amperolyzer isnt that helpfull it tells you only how to use the program.
I want to look @ the bytes of the signal, if you know what I mean.

like the signal 17 C3 00 00 00 00 00 00

what does it mean? etc.

are there any manuals for this?
Top
  6/7/2010, 5:56 PM
Joined 9/27/2006
Last visit: 5/18/2013
Posts: 3926
Rating:
Rated: Excellent [4.15 out of 5 / rated 619 time(s)]. (619) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello Hezzens;
It would appear that what you are looking for is a combination oscilloscope/protocol analyser.
You could look at Profitrace (and associated products) from Procentec:
http://www.procentec.com/products/#profitrace
It is one of the most powerful Profibus diagnostic tools I have seen in operation.
Hope this helps,
Daniel Chartier
Top
  6/7/2010, 11:07 PM
Joined 8/25/2005
Last visit: 5/8/2013
Posts: 973
Rating:
Rated: Outstanding [3.68 out of 5 / rated 92 time(s)]. (92) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hello Hezzens_Z,

detailed information about the data which are transferred should be found in the documention of your Simodrive.

Whats about the dignostic information within the PLC? Are you sure that the connection is established, ...

Good luck
Sabine
Top
  6/9/2010, 2:43 PM
Joined 8/4/2009
Last visit: 5/17/2013
Posts: 2307
Rating:
Rated: Excellent [4.11 out of 5 / rated 396 time(s)]. (396) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hezzens_Z wrote:
Good morning (if you live in europe ^^)

I have the following problem.
I have 3 pumps with simodrive that is connected on Profibus DP.
My software is working properly and the hardware is installed correctly but my pumps will not work.

So I want to check out the profibus DP signal, so I can determine the problem.
Is there an manual for this?

PS I already have a PG with CP5611 and Amperolyzer V3.0


Hello...

Can you check the profibus cable sheilding and connectors.....have it is  installed properly.

there steps to check the connector and it is already posted in fourm. I am attaching the details of the same

And there is BT200 equipment avialble from Siemens for checking the profibus cable and the connecttor.

Hope this infromation may be useful......

Ekalavya

Attachment: Checking procedure for Profibus Connector.pdf  (30 Downloads)

Please no technical questions by Private Message(PM), use the FORUM!!!!!

Top