Technical Forum

Process Control System - QUADLOG

Degraded system bit ?

Thread Starter: Bey   Started: 6/6/2008 10:35 AM   Replies: 2

« Previous thread Next thread »
Page 1 of 1 (3 items)
  6/6/2008, 10:35 AM
Joined 5/27/2008
Last visit: 1/27/2011
Posts: 10
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Hi everybody,

Can you please tell me what is the difference between the bit : Redundancy degraded bit from RSCALRM bloc and system degraded from TOT_IOSD ?

If yes , why there are two informations !! and which one should I use in my trip logics to comply with TUV ?If no! what is the difference ? Thanks in advance. 



=== Edited by Bey @ 6/6/2008 10:36 AM [GMT ] ===


Top
  6/6/2008, 5:21 PM
Joined 12/20/2005
Last visit: 4/23/2013
Posts: 78
Rating:
Rated: Excellent [5 out of 5 / rated 3 time(s)]. (3) 
Users with special expertise supervising conferences
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Bey,
The documentation for the TOT_IOSD function block says:

The DEGRAD output indicates that a critical class 4 error exists in the system or the auto-shutdown latch has not been cleared. Repair action should be taken in a timely manner whenever critical errors are reported. If the system is degraded, redundancy has been lost and a failure on the remaining functional side of the system will cause a system failure. Whenever the system is degraded, the following actions take place:

1. The DEGRAD output is set to TRUE.

2. Error code SSC 27, EC 20 (FB logic has disabled system switchovers) is reported indicating the switchovers based on error counts are disabled.

3. Error code SSC 30, EC 06 (QUADLOG ACM/CCM Shut Down module outputs) is reported for SD controller if AUTOSD is enabled.

So without getting too deep into this it seems that if the DEGRAD output is TRUE, the RSCALRM bit 10 would also be TRUE, HOWEVER there MAY be scenarios where the opposite could occur, RSCALRM bit 10 might be TRUE but DEGRAD is FALSE.

If you need to know for sure, I would contact Siemens Technical Support, however if it were me I'd follow the recommendations in the QUADLOG Safety Manual and stick to using the TOT_IOSD to trip my shutdown logic: http://support.automation.siemens.com/WW/view/en/23447258


Regards,
RJP

Top
  6/6/2008, 11:16 PM
Joined 5/27/2008
Last visit: 1/27/2011
Posts: 10
Rating:
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
Rated: no ratings [0 out of 5 / rated 0 time(s)]. (0) 
RJP,
It will be great if you confirm me the difference between the two bits., and all the possible scenarios.
Thanks in advance.
Bey.